I am trying to understand how 'stiff' the line-neutral voltage will be in a wye-wye transformer built on a common 3 leg core, with only 3 wires supplied to the primary.
I know that in the case of a wye-wye transformer built out of 3 separate single phase transformers, the 'neutral impedance' would be very high. The reasoning is to consider the arrangement with a single phase load connected line-neutral on the secondary. This secondary current requires primary current on the connected leg. However there is no secondary current on the other two legs of the wye, and thus the primary current on the other two legs of the wye is just magnetizing current.
But in the case of a common 3 leg core, each secondary coil interacts with all three primary coils, so current on only one of the secondary coils can cause current on all of the primary coils.
I was hoping for a pointer to how to calculate this case.
Thanks
Jon
I know that in the case of a wye-wye transformer built out of 3 separate single phase transformers, the 'neutral impedance' would be very high. The reasoning is to consider the arrangement with a single phase load connected line-neutral on the secondary. This secondary current requires primary current on the connected leg. However there is no secondary current on the other two legs of the wye, and thus the primary current on the other two legs of the wye is just magnetizing current.
But in the case of a common 3 leg core, each secondary coil interacts with all three primary coils, so current on only one of the secondary coils can cause current on all of the primary coils.
I was hoping for a pointer to how to calculate this case.