Specifications required a Delta-Wye Grounded transformer to serve a distribution panel with both three phase (208V) and single phase (120V) loads.
Contractor installed Wye-Wye grounded transformer (leftover at the distributor), where the secondary Xo is grounded, but the Xo of the Primary is not grounded. In addition, a neutral was not pulled with the primary conductors.
Other than the obvious of being used outside of the manufacturers instructions, what are the other downsides. Owner likes the contractor and wants to keep it :roll: .