brian john
- Kilmarnock, Va
- Retired after 52 years in the trade.
I have a UPS that is 480 (3 phase 3 wire input) and 208/120 3 phase 3 wire output. There is an external 2 circuit breaker bypass cabinet and a factory furnished 208/120 wye to 480/277 wye step up transformer.
This facility is 208/120 wye throughout. The Y/Y transformer is for stepping up the input to the UPS. XO/HO connection is a welded bus common connection.
Normally with a 208/120 wye to 480 delta (back fed transformer) one does not install a neutral to the XO. Does anyone feel a neutral is need for this installation?
Without a neutral the XO/HO terminal would need to be grounded, with a neutral on the load side this connection would be grounded at the main service for this facility.