- Location
- Connecticut
- Occupation
- Engineer
What about this table's note 3, if this criteria is met OCP can be up to 6 times the rated current.
Yes, if the transformer was equipped with "coordinated thermal overload protection" and has an impedance of not more than 6%, then the primary OCPD could be 1000A. The primary conductor ampacity would have to be at least 1000.
But I don't see anything in the OP that suggests the xfmr has "coordinated thermal overload protection."