Yes, if the transformer was equipped with "coordinated thermal overload protection" and has an impedance of not more than 6%, then the primary OCPD could be 1000A. The primary conductor ampacity would have to be at least 1000.
But I don't see anything in the OP that suggests the xfmr has "coordinated thermal overload protection."
I have a 400 amp buss that is a 3 phase 4 wire system rated for 277/480 volts. This application is suppose to feed a 150kva step down transformer = 480-120/208 volts 3 phase 4 wire. I'm having diffuculties trying to figure out the feeder conductors aswell as over current protection for this particular installation. Where do I start?
You also won’t see “Primary and secondary protection” from T450.3B
- I hope you’re not rubbed or bothered; the OP is asking how to feed and protect this XFMR. There are great answers early on revealing excellent methods of how to arrive at this info answering to
start with the load.
You pointed out some good stuff and what’s evolved topically is this XFMR’s OCP can be 1000A its primary feeder would have to be sized per OCP, a panelboard is not sized per XFMR but must be sized at least for it’s specific calculated load and fed as such and it will also include OCP (it can be 2000A). The only thing actually related to the XFMR in this method is the primary circuit and XFMR protection, not the secondary conductors or downstream items.
Why stop at assuming only part of T450.3B?