SHORT CIRCUIT PF % = R / Z. and. Z can not be calculated from the X /R ratio. The value of R or X must be known to calculate Z from X / R.
Bottom line here is LV circuit breakers need to be derated if the short circuit X / R is greater than 15. There is a table for this correction factor.
When PF % O.15 is given with X/R 6.6 as lv circuit breaker test values, this turns out to be useless information. And caused my mental block. Now unblocked.
Bottom line here is LV circuit breakers need to be derated if the short circuit X / R is greater than 15. There is a table for this correction factor.
When PF % O.15 is given with X/R 6.6 as lv circuit breaker test values, this turns out to be useless information. And caused my mental block. Now unblocked.