Hello all!!!
I was wondering if anyone knew how to calculate the load for a Xray Machine Generator?
Our service is a 120/208 3PH

Here are the specs on the generator

Momentary Current 185A @230V
Momentary Power Consumption 43 Kva

Thanks
 

spsnyder

Senior Member
I come up with 43 kVA, (single phase). What are you asking for?

Your question give the load. Are you asking for OCP / Conductor sizing?
 
Last edited:

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Look in NEC 517 if it is a health care xray machine. If memory serves me right, the first xray machine is calculated at 50% of the momentary demand.

If its 3 phase, the momentary demand would be about 67KVA.

Steve
 
I guess the real question I am trying to get at is if a 225A service is big enough for this urgency care clinic

2500 square feet
50 duplex receptacles
7 ton air conditioning
x ray machine 150A momentary draw
gas heat
gas water heater
 