X Ray Machine
Hello all!!!
I was wondering if anyone knew how to calculate the load for a Xray Machine Generator?
Our service is a 120/208 3PH
Here are the specs on the generator
Momentary Current 185A @230V
Momentary Power Consumption 43 Kva
Thanks
I come up with 43 kVA, (single phase). What are you asking for?
Your question give the load. Are you asking for OCP / Conductor sizing?
Look in NEC 517 if it is a health care xray machine. If memory serves me right, the first xray machine is calculated at 50% of the momentary demand.
If its 3 phase, the momentary demand would be about 67KVA.
Steve
I guess the real question I am trying to get at is if a 225A service is big enough for this urgency care clinic
2500 square feet
50 duplex receptacles
7 ton air conditioning
x ray machine 150A momentary draw
gas heat