R Bob
Senior Member
- Location
- Chantilly, VA
I installed a 100a sub-panel in a single family dwelling fed from a auto xfer switch that is fed from the main service panel and a stand-by generator.
The conductors were sized based on T310.16. I used #1 cu THHN protected by a 100a CB in the main service panel and a 100a CB in the generator.
The inspector comes and says "nice work"....he gives me a green sticker.
He asks why I used #1 cu. I explained my rationale as I did above. He says that I could have used T310.15(B)(6) to size the conductors which would have been #4 cu. He directed me to Article 215.2(A)(4)[NEC2002] and 310.15(B)(6).
I think that Article 215.2(A)(4) is specifically referring to the feeder for an apartment/condo or mobile home and does not apply to my situation. (???)
310.15(B)(6) references the feeder conductors that serve as the main power feeder. The article goes on to define the main power feeder as the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboard(s).
To me, the main power feeder is the conductors originating at the service disconnect(s) and terminating at the panelboard(s). (???)
What do you guys think?
Worst case scenario...I over engineered it a bit!
The conductors were sized based on T310.16. I used #1 cu THHN protected by a 100a CB in the main service panel and a 100a CB in the generator.
The inspector comes and says "nice work"....he gives me a green sticker.
He asks why I used #1 cu. I explained my rationale as I did above. He says that I could have used T310.15(B)(6) to size the conductors which would have been #4 cu. He directed me to Article 215.2(A)(4)[NEC2002] and 310.15(B)(6).
I think that Article 215.2(A)(4) is specifically referring to the feeder for an apartment/condo or mobile home and does not apply to my situation. (???)
310.15(B)(6) references the feeder conductors that serve as the main power feeder. The article goes on to define the main power feeder as the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboard(s).
To me, the main power feeder is the conductors originating at the service disconnect(s) and terminating at the panelboard(s). (???)
What do you guys think?
Worst case scenario...I over engineered it a bit!