don_resqcapt19;1107633]The protection for this transformer is sized per Table 450.3(B) and that table does not require secondary overcurrent protection when the primary protection is sized at 125% of less of the rated primary current.
Earlier in this thread it was said you could land these secondary conductors on any size OCPD as long as they were sized to be equal to or greater than said OCPD. ( Not in those words exatly)
As I said in my last post if this is a multi volt secondary the line to neutral currents pose a problem for the primary OCPD to protect the secondary windings and conductors.
1:4 voltage ratio and 4:1 current ratio with the line to neutral load....
It would take 80 amps or greater on a line to neutral load to trip primary OCPD.
The secondary of this transformer is 15 kVA 120/240.
150000 / (240 x 1.73) = 36.12 FLC x 1.25 = 45.15
So at 36 amps at 240 volts we have 18 amps on the secondary.
The primary of this transformer is 15 kVA 480
15000 / (480 x 1.73) = 18.06
This is a 1:2 voltage ratio primary to secondary.
But this is a multivolt secondary
1:4 voltage ratio with 120 volt load
That means if there is a unbalance it would take more than the rated FLC of the secondary to trip the primary OCPD by 2 fold.
80 amp 120 volt load to trip the 20 primary OCPD
With anything larger than a 45 amp OCPD on the secondary the transformer is not properly protected.
The math does not lie
As long as my math is correct
Once again I am not trying to have a pissing contest bit this is the way I understand the rules...It's all about the math. That is what 240.4 (F) and 240.21 (C) (1) is stating.
The main difference is single voltage secondary or multi voltage secondary.