On a step down XFMR 480 Delta to 208 Y you need to bond the XO to ground or there is no ground fault path on the output side. I saw a step UP XFMR today that was 208 Y on the input and 480 Delta on the output, there is nothing connected to the XO. There is just an equipment ground run through the conduits and bonded to the boxes. How is the fault current path made in this configuration ?