We are purchasing a 300kva 3 phase 2400 volt delta primary to
480/277y secondary.The only loads supplied will be 3 phase 480
volt motors and one 480/277 primary to 120/240 secondary 15kva
xfmr.We do not want to ground xo of the secondary 480/277y of
the 2400 volt xfmr as there is no need for a neutral conductor
in our circuits.We also have ground detection lights on our 480
system which needs an ungrounded system to work properly.Is it
legal not to not ground the wye secondary system.(250.20
B2).Will it cause problems to "float" xo?