Sometimes I see a transition from flex to EMT or RGS. That would require an adapter coupling correct?
Yes, and it has a few different names, change over, from to, EMT/Flex coupling, etc. (Photo 1)
In the old days we made them with a rigid coupling and two connectors. (Photo 2)
For multiple raceways we may use a pull box into the side of the transformer. (Photo 3)
In many cases the flex connection is not even needed or required.

Flex Connection.jpgXFMR Flex Connection.jpgXFMR Pullbox.JPG
 
Yes, and it has a few different names, change over, from to, EMT/Flex coupling, etc. (Photo 1)
In the old days we made them with a rigid coupling and two connectors. (Photo 2)
For multiple raceways we may use a pull box into the side of the transformer. (Photo 3)
In many cases the flex connection is not even needed or required.

View attachment 2569237View attachment 2569238View attachment 2569239
Thanks. Great pics. I thought you always had to have flex into vibrating equipment. At least I believe spec often reads that way.
 
Transformer are not considered as vibrating equipment.

Like the way you transitioned into the transformer. Did you cut the inside for entry, or punch KOs for chase nipples? Just curious, I have done it both ways depending on the size of the conductors.
 
Transformer are not considered as vibrating equipment.

Like the way you transitioned into the transformer. Did you cut the inside for entry, or punch KOs for chase nipples? Just curious, I have done it both ways depending on the size of the conductors.
What exactly do you mean? Your referring to the xfrmr enclosure? Curious.
 
Like the way you transitioned into the transformer. Did you cut the inside for entry, or punch KOs for chase nipples? Just curious, I have done it both ways depending on the size of the conductors.
We cut in windows. Here's a few more photos with the windows. The first is from the transformer in post #25. The second is another transformer.

XFMR Window001.jpg
XFMR Window002.jpg
 
Thanks for all the responses. Does the same apply for disconnect switches?
Over 600 amps you might find they just have studs. Can probably find some that way under 600 amps but probably not with commonly stocked items at most suppliers. Usually 400 and 600 amp items will have a lug that accepts either single or double conductors in the sizes that are most commonly used for that ampacity or even at least accept a size bigger for those cases where minimal upsizing is necessary.
 
Regular disconnects always have the lugs attached. For transformers I guess it depends on the way that they're ordered. I've seen them come with or without mechanical terminals. I've never seen them come with crimp on terminals. If you had a job spec that required crimp terminals it would not make sense to buy transformers that had mechanical terminals that would need to be removed and thrown away. This one (75 KKVA) had the terminals attached from the manufacturer.


View attachment 2569231
Off topic but just noticing the GEC leaving the right side, though nothing wrong with it, probably doesn't require the bonding bushing unless the flex is steel or converts to steel pipe/tubing at some point. Otherwise looks to be zinc die cast fitting and aluminum flex.
 
Off topic but just noticing the GEC leaving the right side, though nothing wrong with it, probably doesn't require the bonding bushing unless the flex is steel or converts to steel pipe/tubing at some point. Otherwise looks to be zinc die cast fitting and aluminum flex.
EMT to steel FMC hence the bonding bushing on the GEC. Another view:

IMG_20220405_134420546~2.jpg
 