No. Your question was specific to ground fault protection of transformers. Secondary side GF protection almost never has any impact on the primary side protection requirements. For the majority of installations the primary side sees a secondary side GF as if it was a load.By this I assume you mean protecting the secondary conductors as well as the ability to divide the secondary into multiple different branch circuits?