Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
225AF WITH 110AT breaker feeding 75 kva xfrm(277/480v primary). Secondary of xfrmr feeds two panels, both 125A main breaker, right next to each other. The feeder to those panels has a tap. The primary conductors are not my concern, the secondary are.

They sized the secondary conductors to be 4 #1’s. That seems incorrect.

Thanks.
 
225AF WITH 110AT breaker feeding 75 kva xfrm(277/480v primary). Secondary of xfrmr feeds two panels, both 125A main breaker, right next to each other. The feeder to those panels has a tap. The primary conductors are not my concern, the secondary are.

They sized the secondary conductors to be 4 #1’s. That seems incorrect.

Thanks.
#1 ampacity is 130 Amps. They terminate on a 125 A CB. As long as there are two sets of conductors, one going to each PB, I don't see an issue.
 
i thought because of the ta

they are tapping one set to 2 two sets to feed both panels .
You're saying there is one set of conductors connected at the transformer secondary that runs to a box or trough, where a splice is made to feed both panels? That wouldn't be Code compliant.
 
Transformer secondary conductors are just that, they are not feeder conductors. Different rules on transformer secondaries
 
Transformer secondary conductors are just that, they are not feeder conductors. Different rules on transformer secondaries
There are times I wish that 240.21(C) was not in the same section as the 'tap rules'. But 'ease of use' is rarely a reason the NEC gets changed.
 
You're saying there is one set of conductors connected at the transformer secondary that runs to a box or trough, where a splice is made to feed both panels? That wouldn't be Code compliant.
well that’s the ways they show it on the single line drawing . if that’s the case you can’t splice one set of secondary to feed two panels ?
 
well that’s the ways they show it on the single line drawing . if that’s the case you can’t splice one set of secondary to feed two panels ?
But you can run two sets of secondary conductors from the transformer, with one set going to each panel, as long as you comply with one of the rules in 240.21(C).
 
But transformer secondary conductors ARE feeder conductors (or maybe in some rare cases, branch circuit conductors.)
While they may meet the definition of feeder conductors, you have to know and understand that they are a special case, and use the term transformer secondary conductors to apply the code. If you just call them feeder conductors, you won't get to the rules in 240.21(C) that cover the overcurrent protection of those conductors.
 
Sure you would. 240.21 applies to all feeder conductors.
If you call them feeders you will stop at 240.21(B) Feeder Taps, and not get to 240.21(C) (C) Transformer Secondary Conductors.
If the code user thinks they are feeders they will look only at (B) when then need to be looking at (C).
 
If you call them feeders you will stop at 240.21(B) Feeder Taps, and not get to 240.21(C) (C) Transformer Secondary Conductors.
If the code user thinks they are feeders they will look only at (B) when then need to be looking at (C).
They're not feeder "taps", so 240.21(B) wouldn't apply. So move on to 240.21(C).
 