Not if that's all it says. No other markings like XHHW or USE?Is Type XLPE insulation not recognized by the NEC?
I’m trying to find it for conduit fill and don’t see it in any of the tables.
Thank you.
That’s what’s listed in the Mfgrs cut sheet. Don’t have the actual wire in front of me.Not if that's all it says. No other markings like XHHW or USE?
You could run the calc with type USE, as that would be the thickest insulation. If it's aluminum, then of course it's probably compact, but it might be compressed stranded also which is going to be a little larger.That’s what’s listed in the Mfgrs cut sheet. Don’t have the actual wire in front of me.
Trying to determine if I can get 3- 250 MCM and 1 -3/0 conductor in a 2” EMT.
Will be used as a 4’ sleeve , not pulling through a complete run.
Only have 2” knockouts to work with on disconnects.and need to protect where it emerges from the ground.
All gonna depend on what the conductors are marked as.Looks like it fits with xhhw, but not RHH/USE
But if it's just a sleeve I think you're fine with either.
Performance Wire and Cable utilizes XLPE insulation on USE-2 wires, RHW-2 cable, and RHH cable.