Re: XMER PRIMARY&SECONDARY PROTECTION
Linda, method 2 is for when you do provide secondary protection, then you can change the size of the primary protection.
jschultz, the correct answer is transformers do not need protection - stop looking in 450, conductors do need protection start looking in 240.
One example: Industrial application, 75KVA 480V primary to 208Y/120 secondary transformer, output rated for 208A, conduit, ambient, and terminations per 75C column.
Per 240.4(F) conductors need protection. 240.21 says the protection does not need to be at the begining of the conductors. 240.21(C)(3) will allow (3) 25' long feeders of 350kcmil (310A max.) to (3) wall mounted 100A main breaker panelboards.
[ April 21, 2004, 09:07 AM: Message edited by: jim dungar ]