Re: y to delta ...208v to 480v sec
I recently did an installation as stated above. The ITE / Siemens installation guide does show wiring diagrams for a step-up installation. All terminal are labeled HV or LV, not primary / secondary. The installation was corner ground as agreed upon with the local AHJ. The main reason we chose to use a "Step down" transformer for this installation was delivery time as this was a stock unit and only 480 volt, 3 phase was required.
I am sure that major transformer manufacturers would not have publications on alternate wiring diagrams if not properly tested & listed for the application.
Most of my electricains have never seen a corner grounded installation and they were all amazed at the lack of explosion when energized.
I recently did an installation as stated above. The ITE / Siemens installation guide does show wiring diagrams for a step-up installation. All terminal are labeled HV or LV, not primary / secondary. The installation was corner ground as agreed upon with the local AHJ. The main reason we chose to use a "Step down" transformer for this installation was delivery time as this was a stock unit and only 480 volt, 3 phase was required.