meternerd
Senior Member
- Location
- Athol, ID
- Occupation
- retired water & electric utility electrician, meter/relay tech
In the 21 years that I have been in the industry providing transformers to industrial/commercial customers I have never once was required to provide a Y-Y transformer. To the best of my knowledge it is common for utilities to use Y-Y transformers for transmission but for a service entrance D-Y are commonly used.
Is this a transformer that you are required to purchase and will be owned by you? How about the utility metering? I am assuming that there will be CTs amd PTs involved. Are they on the 13.8kv side which they probably are?
I agree with you to question the Y-Y transformer requirement.
I've been in the utility industry for 40 years. In my experience, it's just the opposite of your statement. Transmission is almost always Delta, since running 4 conductors is MUCH more expensive than running three. Once the transmission hits the substation, it is usually wired Delta Primary and Grounded Wye secondary. The 4 wire grounded Wye distribution system is then run to service transformers. Most modern systems (underground especially) are Wye/Wye. In the west, the most commn distribution voltage is 12,470/7200.
As mentioned, the primary neutral and secondary neutral of medium voltage transformers have a common H0 / X0 terminal that is externally bonded to the enclosure and ground. The neutral is connected to a grounding electrode. The bond to the common neutral is removable to allow megger testing.