Hello,
I'm a contractor dealing with mainly interior projects.
I recemtly completed a home gym with new wiring for receptacles and lighting.
Permit required arc fault breakers.
My electrician put in sub panel . We have had standard breakers in for the duration. Upcoming inspection had me install the AFCI breakers.
2 20 amps for the receptacle circuits
1 15 amp for the lighting
Receptacles are fine... lighting keeps tripping
The home run goes to a junction box where its tied to 2 runs. One goes to a 3 way switched stairwell lights.
Other goes to a double switch controlling 11 recessed lights.
All recessed lights have LED bulbs, one of the stairwell lights is an incandescent bulb.
Its tripping with various conditions.
I've separated the 2 lined individually and both areas will trip the AFCI breaker
If I turn off the lights then reset the breaker then turn on the lights they will stay on, until a switch is operated then it trips.
I connected the home run to one of the 20 amp AFCI and it holds
I've also replace the breaker...same result
It's a Siemens panel and Siemens breakers3
They have LED diagnostics. The LED is indicating an overcurrent trip.
On a standard 15 amp breaker, it holds.
I've been back and forth with my guy on the phone and we cant isolate a problem.
We are supposed to look at it soon but any ideas would be appreciated.
Thanks
I'm a contractor dealing with mainly interior projects.
I recemtly completed a home gym with new wiring for receptacles and lighting.
Permit required arc fault breakers.
My electrician put in sub panel . We have had standard breakers in for the duration. Upcoming inspection had me install the AFCI breakers.
2 20 amps for the receptacle circuits
1 15 amp for the lighting
Receptacles are fine... lighting keeps tripping
The home run goes to a junction box where its tied to 2 runs. One goes to a 3 way switched stairwell lights.
Other goes to a double switch controlling 11 recessed lights.
All recessed lights have LED bulbs, one of the stairwell lights is an incandescent bulb.
Its tripping with various conditions.
I've separated the 2 lined individually and both areas will trip the AFCI breaker
If I turn off the lights then reset the breaker then turn on the lights they will stay on, until a switch is operated then it trips.
I connected the home run to one of the 20 amp AFCI and it holds
I've also replace the breaker...same result
It's a Siemens panel and Siemens breakers3
They have LED diagnostics. The LED is indicating an overcurrent trip.
On a standard 15 amp breaker, it holds.
I've been back and forth with my guy on the phone and we cant isolate a problem.
We are supposed to look at it soon but any ideas would be appreciated.
Thanks