hydeisland
Member
- Location
- San Diego,CA
Today I got into a conversation with a PM from an integrator I do contract work for. He started talking about "weebs" and I told him how much I didn t like them and I prefered the "old" method of using #10 bare copper for the egc. He then told me I'm out of code compliance because of art. 250.120(C) requiring a #6. I disagree with him because I believe being underneath modules is "where protected from physical damage". Anytime my egc is exposed I use conduit sleeves etc. The only time I do not use sleeves is when it is underneath the modules themselves. In 4 years of doing PV I have never been called on this. Do I now need to start using these "weebs"? I cannot afford to start bonding with #6 and buying the proper rated lugs to go with it.