You guys with your great experience and knowledge have me convinced. I truly appreciate the great help from this amazing website.
If I pull 2 boats do you strongly recommend 8 different colors???? Brown Orange Yellow White for boat 1......Red, Black, Blue Gray for boat 2 ???
I thought the breakers are all rated for continuous???? Perhaps not a given. Must I make this a specific requirement??? And pay more of course like you say......
Thank you. I'd pull 2 sets of B,O,Y,W/Gr. One set (boat) of spools on one rod, the other on a second. I dont think you can use red, black, blue if you have a 120/208 or 120/240 service also in the building
I looked up 100% breakers. SQD makes them, C suffix indicates the 100% use. Here is one such 277V 20A:
https://www.southlandelectrical.com/ItemDesc.asp?IC=FY14020C-NS
Mains and the like may be rated continuous, but most breakers are not. You'd have to spec them. They might not be available for your existing panel.
One other thing; for existing conduits, it's a good idea to blow em out before pulling in wire. A tank of compressed air is cheap, or just use an air compressor with the rubber tip on it.
The existing EMT, did it go to previous MH/HPS lights? If so, are the existing conductors still in place?
eta: All breakers can handle their listed ampacity. iow, if you calculate a 19.999A load, you can use a 20A breaker... or even a 20.4A load, since fractions less than 0.5 are ignored. However, if that load is expected to run 3 or more hours, you are limited to 80% of the breaker's capacity (16A for a 20A), unless you get a breaker designed for 100% loading.
If you wanted to get creative, you could run all your lights thru a timer that would let them run 2:59, cut off for one minute, then restart, avoiding the continuous load. You'd probably never get another lighting job ever again tho lol.