Well, I think there's a recipe for chicken soup hidden in 300.9, too, you just have to read enough into it.Those are not the questions from Electrical Contractor Magazine that I referenced.
Here is the text and the link
http://www.ecmag.com/index.cfm?fa=article&articleID=11348
NM cable for outside lights Can I use NM cable to feed the outside lights and receptacles in a dwelling unit?
No, Section 300.9 was added to the 2008 NEC, and it specifically shows that the interiors of raceways and enclosures installed in above-grade wet locations are considered to be wet locations and require conductors suitable for use in wet locations in accordance with 310.8. NEC 34.12 does not permit Type NM cable to be used in a wet or damp location.
I don't see one mention of enclosure in that section.300.9 Raceways in Wet Locations Above Grade. Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.8(C).
Further, how on earth would we recess boxes into the sides of houses? Use 3/0 bell boxes?