I got the ECM Code Watch newletter today and want to make a comment on Mike's contribution.
The drawing shows a panelboard installed at a stairway mid landing. Mike is correct in that the NEC allows this installation. The big "BUT" here is that the IBC does not permit this when installed in an enclosed stairwell; called an exit enclosure in the IBC. As pictured that would be ok in a dwelling unit, but not a commercial bldg 90% of the time.
My point is that the NEC rules are not the only thing an electrician needs to know.
In my opinion there should have at least been a mention of what is required by the building code. You can get in real trouble if you blindly follow the NEC.
The drawing shows a panelboard installed at a stairway mid landing. Mike is correct in that the NEC allows this installation. The big "BUT" here is that the IBC does not permit this when installed in an enclosed stairwell; called an exit enclosure in the IBC. As pictured that would be ok in a dwelling unit, but not a commercial bldg 90% of the time.
My point is that the NEC rules are not the only thing an electrician needs to know.
In my opinion there should have at least been a mention of what is required by the building code. You can get in real trouble if you blindly follow the NEC.