I am coming into this one a bit late. OK, here is some info that comes to my memory. But I can?t assert the percentage of truth in any of it. My last days of ?haze grey and underway? are 22 years in the past.
1. US Navy shipboard 120 volt systems are not grounded.
2. There is a ground detection system that will tell you if a single phase has an undesired connection to the hull. It is checked at least once an hour. It is possible that more modern ships have an automatic ground detection system, but I have no facts to offer on that topic.
3. All non-current carrying metal parts of all electrical systems are bonded to the hull. This could be with welds, bolts, or bond wires.
4. An overcurrent condition will trip the breaker in the due course of time, just as it would in a shore facility.
5. A short circuit will clear by immediately tripping the breaker. But that?s the same as shore facilities. By ?short circuit,? I am referring to Phase to Neutral or Phase to Phase.
6. The first ground fault will not clear, as several members have already described. The intent is that that first ground fault should be detected and isolated, before the second ground fault occurs.
7. The reason for an ungrounded 120 volt system is to maintain operation under battle conditions.
8. You can be electrocuted by touching a hot wire in an ungrounded system. Tom was right, and his reason was also right. But he misspelled ?capacitance.?
9. Fault coordination (i.e., the breaker nearest the fault trips first) is a design criterion. I have never had the opportunity to perform a fault coordination study for a vessel, Navy or otherwise. So I can?t give any information on how well it works.
10. During the time that I worked in the Marine Engineering arena, the most significant difference that I noticed in non-navy ships has to do with oil tankers. Any 120 volt branch circuit that has wires cross through what we would call a ?Class I Location? must have a breaker with a switched neutral. It?s like a 2-pole breaker, but the second pole does not connect to the ?other? phase. Instead, the second pole connects to the neutral bar. This requires a special construction of the panel.
I guess that?s enough sea stories for now.
Charles E. Beck,
Commander, USNR, Retired.