First some background. A site had 480V 3-phase service. One of the feeders went to a transfer switch to provide back-up power from a 480V 3-phase generator. The loads were from some 3-phase air compressors, a large 480V-120/240 split phase transformer feeding an MCC, and a very small 480V-120/240 split phase transformer feeding a panelboard with hardly any load.
One fine day during a planned outage the genny and transfer switch did their job, then the genny tripped out a minute later. Upon investigation it was noted that it tripped on current imbalance, which was set at 25%. (Somehow this had gotten changed from the original 75%). The only 3-phase demand was the 3 air compressors which were programmed to wait a few minutes after a power restoration and then come on one at a time as needed. No surprise it tripped with the low imbalance trip and nearly no load on one of the legs.
My suggestion was to install a 277V-120/240 split phase transformer and feed both the small panel board mentioned and a larger one fed from the MCC. This would remove some of the load from the 2 legs feeding the large transformer and move it to the remaining single leg going to the additional transformer. I doubt they did so and probably just left things like they were. (Been job hopping lately...)
But I got to thinking about this and have a question. Let's say the change was accomplished and the large transformer drew 50 amps on phases A to B while the small transformer drew 50 amps on phase C to neutral. I am used to thinking that if all the legs draw the same amps, there is no neutral current at the source. Or is that only the case with split phase?
One fine day during a planned outage the genny and transfer switch did their job, then the genny tripped out a minute later. Upon investigation it was noted that it tripped on current imbalance, which was set at 25%. (Somehow this had gotten changed from the original 75%). The only 3-phase demand was the 3 air compressors which were programmed to wait a few minutes after a power restoration and then come on one at a time as needed. No surprise it tripped with the low imbalance trip and nearly no load on one of the legs.
My suggestion was to install a 277V-120/240 split phase transformer and feed both the small panel board mentioned and a larger one fed from the MCC. This would remove some of the load from the 2 legs feeding the large transformer and move it to the remaining single leg going to the additional transformer. I doubt they did so and probably just left things like they were. (Been job hopping lately...)
But I got to thinking about this and have a question. Let's say the change was accomplished and the large transformer drew 50 amps on phases A to B while the small transformer drew 50 amps on phase C to neutral. I am used to thinking that if all the legs draw the same amps, there is no neutral current at the source. Or is that only the case with split phase?