If you are using a ZSCT, you must be using a Zero Sequence input to a protective relay of some sort. Depending on the sensitivity you are looking for and/or the type of system it is connected to, the ratio of the ZSCT is not related to the primary current, it is related to the possible zero sequence current that you will allow before tripping the relay. So for instance if you are using a Multilin 750 FPR or a 469 MPR, the ZSCT recommendation is 50:5 for solidly grounded systems, 50:0.25 for resistance grounded systems, because your current to ground will be restricted by the NGR.
Don't confuse this with Residual GFP, or GFP vs GFCI, those are all different issues. If you are required to provide ZSGFP, you must have a system that is looking for the input from it, and THAT system is what should dictate the selection of the ZSCT. Once you know that, the only other issue is the size of the window opening so that you can get all of your cables through it.