Bugman1400
Senior Member
- Location
- Charlotte, NC
I would like to clarify a few items. The 2000:1 CTs mentioned previously are not typical CTs that are connected to the GE Multilin. The CTs mentioned in the Multilin manual is a specialized Ground Fault CT and has a small twisted pair secondary wire that is connected to the back of the Multilin. I think this CT is typical red or orange in color. This is in contrast with typical window type 50:5 CTs that have a true 5A secondary. For both types, you need to make sure the phase conductors go through the CT and the ground wire does not.