zero sequence voltage for line to line voltage
steve66 said:
So you're saying the zero sequence voltage is always zero, no matter what?
If so, then what would be the point in even having something called a "zero sequence voltage". It would just be another name for "zero".
Again, I remember almost nothing of sequence voltages, but I still wonder if the equations you are using aren't limited to sine waves that are all the same frequency.
At the very least, I'm betting those equations can't be used for waveforms which are changing in frequency.
Steve
You can certainly have zero-sequence voltages when measuring phase-to-neutral voltages. This is the normal case. It's a little unusual to calculate the sequence voltages on a phase-to-phase basis.
If you connect the secondaries of VTs in broken delta, with the primaries connected grounded wye, the voltage across the broken delta is the sum of the phase-to-neutral voltages. This equals 3 times the zero-sequence voltage on a phase-to-neutral basis. This is not the sum of the phase-to-phase voltages.
Sequence calculations do assume sinusoidal quantities of the same frequency, but you could make separate calculations of each component frequency. The sum of three voltages measured in a closed manner is zero, whether or not this technically is a zero-sequence voltage. It is a matter of definition of what is being measured.
I don't care if they are even three phases of a single system. Or even if there are three points. If you measure the voltage VXY from Point X to Point Y, voltage VYC from Point Y to Point C, voltage VCM from Point C to Point M, and voltage VMX from Point M to Point X, then VXY+VYC+VCM+VMX=0.
As I recall, the purpose of symmetrical components is to represent, in a symmetrical form (simpler math) a non-symmetrical set of three phase vectors.
Start off with the non-symmetrical set of three phase vectors -- they are each a slightly different magnitude and they aren't exactly 120 degrees apart from each other. The fact that they sum to zero is looking at the wrong point.
The non-symmetrical set of three phase vectors can be represented by the positive and negative sequence symmetrical vectors (that are exactly 120 degrees apart and each of equal magnitude) and a set of three vectors that are of equal magnitude and equal direction - the so called zero sequence.
Because the total zero sequence vector is three times the zero sequence component in any one phase, it looks disproportionately large.
Why is this looking at the wrong point? To have no zero sequence voltage, the three L-L voltages must sum to zero.
Could you elaborate how looking at this is better? Does this help explain why or why not nisri is getting zero sequence voltages or were you referencing something different? I'm still having to think carefully through some of this stuff to get it clear in my head. I'm slow but I'll get there eventually. Thanks.
Mivey,
It's been a long while since I worked with this.
As I recall, for this set of line to line 3? voltages, if the voltages are exactly 120? apart and of equal magnitude, that is, they are originally symmetrical, then the zero sequence vector goes to zero.
If the line to line 3? voltages are not symmetrical, there will be a non-zero zero sequence voltage for each line to line voltage. The math of symmetrical components says that the magnitude of each zero sequence voltage, for each line to line voltage, will be equal and that each zero sequence vector's direction will be the same.
I suspect Nisri's field data is not symmetrical at all times. He mentions sags. . .on one, two or all three lines? Of equal of differing amounts?
Assuming that the calculations are coded correctly, then the zero sequence magnitude nearing, or exceeding, either the positive or negative sequence magnitudes indicates a fair lack of symmetry in the line to line voltages in the field data.
...indicates a fair lack of symmetry in the line to line voltages in the field data.
Thanks. I agree that something is going on. Nisri has not answered back with the input values so we may never know.
I was also thinking about using the line-line values. I was doing some homework and found where Blackburn (Protective Relaying) was talking about using only line-neutral for the sequence quantities:
"There is an exception for voltage connections, whereas while in the power system line-to-line voltages are commonly indicated, in symmetrical components they are always given as line-to-neutral (or possibly line-to-ground)".
I have whipped out my Wagner & Evans to see if I can find reference to non-sinusoidals. It is slow reading but good reading at the same time.
Hi guys..
Wow, there are so many opinions regarding to this line-to-line zero sequence voltage. Sorry for the late responds. I was at my hometown for the last 3 days. Sorry guy.
As I go through all the opinions, and read the last email posted by al hildenbrand and mivey, I decided to check back the data. This is one of the data that I used for my software:
Vab= 0.580 pu with angle 114.38 degree
Vbc = 0.579 pu with angle -127.89 degree
Vca = 0.584 pu with angle -4.3677 degree
Seems that there are something not right in the data since the difference between the angle of Vab and Vbc is about 240 degree and the difference between the angle of Vab and Vca is about 119 degree (almost 120 degree).
I think the correct data is the Vbc should delay Vab with 120 degree and Vca delay Vbc with 120 degree.
But will the angle effect the value of the zero sequence voltages?
P/S: Thanks guy for all the opinions and responds. Sorry to give a very unclear question (without the data values), but your opinions and suggestions are highly appreciated. TQ :smile:
Oh, I forgot to informed that the signal contains sag or swell. Thus, the frequency, angle and magnitude will be different during the event. I think steve might be right. The zero sequence voltage of the signal give the nonzero value only during the event. The value of the zero sequence voltage are zero when the voltage is in the normal condition (without sag or swell). So, I think that is the reason why the value is not zero. As mentioned by mivey the phasor triangle of the delta votages should be closed, so that the value of the zero sequence voltage will be 0. Since the event (sag or swell) change the magnitude, frequency and angle of the signal, the phasor triangle of the delta voltages wont be in a close form anymore, thus giving a non zero values for the zero sequence voltage.
Thank you guys for the opinions and informations. Well, I feel a bit stupid for asking this question. Sorry guys..But I got a lot of informations and knowledges about this symmetrical component from this forum, quantatively and qualitatively. Thanks everybody. Thank you very much..:D :D :D
nisri said:
Hi guys..
If you are defining Vab in the usual sense of voltage from b to a, then the phasors are in reverse sequence, but the angles between them are about 120 degrees. Vab is followed by Vca. Vca is followed by Vbc. Vbc is followed by Vab.
The calculate zero-sequence voltage is 0.017 @ 115.3?
To get a phasor voltage from discrete (instantaneous) measurements requires more than one measurement. You need a lot of discrete measurements in each cycle to extract harmonic components. The phasor measurement given would be the fundamental component only - the entire spectrum of a distorted voltage cannot be expressed as a single set of phasors. If there are sags or swells, then the phasor components are also changing with time. The summation of line-to-line voltages will only equal zero if the measurements represent the exact same time. Discrete line-to-line measurements at a particular time should add to zero.
Absolutely. The data is not symmetrical. There will be a zero sequence result that is non-zero.
Test your code by setting your "test data" to a symmetrical set of values.
Say: (using your convention in your post above)
Vab= 0.580 pu with angle 120.0 degree
Vbc = 0.580 pu with angle -120.0 degree
Vca = 0.580 pu with angle -0.0 degree
Plug in the values. The zero sequence should go to zero.
Remember, any three rotating 3? vectors, no matter how asymmetrical, can be represented by two symmetrical sets of three vectors (+ and - seq.) rotating in opposite directions, plus a set of three vectors (0 seq.) of equal magnitude all in the same direction during rotation. When summed together, these three sets of vectors yield the original asymmetrical set of vectors.
calculation method
calculation method
nisri,
The best I can tell, I don't think you can use the sequence transformation on L-L values. This transformation only appears to be valid for L-N values. You can calculate some "V0" value using the transformation on the L-L values, but I'm not sure what the rest of it is telling you. The transformation might give you the zero sequence but the positive and negative sequences won't make sense.
The sum of the L-L values gives you 3*V0. Then you have to find the positive and negative sequence. Do this first by finding the equivalent phase values (Va=1/3*Vcb+2/3*Vac, Vb=1/3*Vac+2/3*Vba, Vc=1/3*Vba+2/3*Vcb). Then run the sequence transformation. The zero sequence will be gone, but you can find the positive and negative sequences. The found neutral point for these equivalent phase values may not be the same as the neutral point you would have for the L-N values.
Now that you have V0 (1/3 of the sum of the L-L values), and V1 and V2, you can calculate the system L-N values.
For example, let's use the data you had:Vab=0.58<114.38, Vbc=0.579<-127.89,Vca=0.584<-4.3677.
The sum yields V0= 1/3*0.029715099<115.3098335 = 0.009905033<115.3098335
The equivalent phases are:Va=0.325321554<145.9900472, Vb=0.339120041<-95.83741718, Vc=0.341943519<22.07956805
This transforms to V1=0.006456056<-112.4053552, V2=0.335331933<144.0455805
Now you can reverse transform this to get: Van=0.342507961<144.2989035, Vbn=0.322328684<-97.65910638, Vcn=0.341400648<25.40078208
This reveals that the system closed delta is Vab=0.570096294<114.3638455, Vbc=0.583532962<-127.0218813, Vca=0.588967036<-5.204912477
Hope this helps
[edit: It would appear that you have a reverse rotation because you have:Van=0.342507961<0, Vbn=0.322328684<118.0419901, Vcn=0.341400648<-118.8981214 which is a-c-b (reverse) instead of a-b-c]
mivey said:
nisri,
Hope this helps
Mivey;
From your msg, did you mean that the symmetrical component of the line to line voltages cannot be obtained directly using the symmetrical components equation of the LN voltages. We need to transform the L-L voltages to equivalent phases, and then use the equation below (got from your previous message) to get the positive and negative sequance.
equation: Vab=(1-a^2)V1 + (1-a)V2
Vbc= (a^2-a)V1 + (a-a^2)V2
We dont have to calculate the zero sequence value since it equal to 0 (is it)?
Mivey, since my data is acb reversed phase, is the equation to get the positive and negative sequence will be the same with the abc phase sequence? :confused:
After thinking about it, you can certainly use the transformation on the L-L values. It should have been clear to me before but I just had a brain clog. It will give you the zero sequence value if the L-L values do not form a closed delta. You will also get a number for V1 and V2 but these will be different from the ones you get if you use the L-N values. The value for the L-L will be higher than the L-N transformation by Sqrt(3). They will also have a 30 degree phase shift, one positive, one negative. For example, with your data:
With the L-L transformation, you get:
V0=0.009905033<115.3098335
V1=0.011182217<-82.40535524
V2=0.580811945<114.0455805
With the L-N transformation, you get:
I guess the best thing to say is that if you have L-N data, use it because it will also give you the zero sequence data. Converting to delta makes you lose the zero sequence info. Getting readings from a closed delta won't show you the zero sequence information. Converting from L-L to L-N may make it easier to see the sequence order. If you build a symmetrical component network, I think you will need the L-N sequences.
No. These equations are for finding Vab and Vbc once you already have the zero, positive and negative sequence. It is just an equation crunch of these (you will find that the V0 term goes away for the L-L result):
Van=V0+V1+V2
Vbn=V0+a^2*V1+a*V2
Vcn=V0+a*V1+a^2*V2
Vab=Van-Vbn
Vbc=Vbn-Vcn
Vca=Vcn-Van
Th following steps are the method to use when you start with L-L voltages and want to use L-N inputs & results. If you start with L-L values, it is easier to use the sqrt(3) factor and the 30 degree shift if you are sure of your sequence order:
Step #1: use the sum of the L-L values to find V0
Step #2: Find the equivalent L-N values from the L-L values by using (Va=1/3*Vcb+2/3*Vac, Vb=1/3*Vac+2/3*Vba, Vc=1/3*Vba+2/3*Vcb).
Step #3: If the rotation of the equivalent L-N set is CW then change to CCW (Vab=-original Vca, Vbc=-original Vbc, Vca=-original Vab) and go back to #1.
Step #4: Transform the equivalent L-N values to get V1 & V2
We don't know if it is zero in the system. With a closed delta, we don't know if there are zero sequence values in the rest of the system because a closed delta will not allow you to see the zero sequence. If we have a set of L-L values that are not closed (a "broken delta") we can sum the L-L values to find the zero sequence (the sum is 3*V0). The L-N sum gives us the same result.
You can use the transformation matrix but you would need to adjust your end results if you want an a-b-c representation (counter-clockwise rotation). This is easy to see when you find the equivalent L-N values.
If it is a-c-b then you realize that Vab is really Vac, Vbc is really Vcb, and Vca is really Vba (swap the "b" and "c"). If we call our original, a-c-b reverse-order L-L vectors Vab', Vbc', and Vca' then we can find the a-b-c rotation vectors by:
Vab = -Vca'
Vbc = -Vbc'
Vca = -Vab'
You could use the transformation matrix on the a-c-b set but you would have to take the end result and add 180 degrees to the zero sequence, and exchange V1 & V2 (I think). I would have to think about the value of transforming set of phasors that are sequenced in a clockwise rotation.
I think this is all correct but I reserve the right to change my mind.
[edit: typo]
rotation vs sequence
I should point out that I am guilty of using the term "reverse rotation" a little carelessly. When charted, the positive, negative, and zero sequence vectors rotate counter-clockwise using the conventional layout. It is the sequence a-b-c vs. a-c-b that is reversed.
The sloppy use of the "reverse rotation" comes from thinking of swapping two leads on a three phase motor to get the motor to reverse rotation. It may not make much difference, but sorry for any confusion.
How can you have three L-L voltages that do not form a closed delta?
:smile: That's part of the real world to math transform jump that doesn't work.
I believe Mivey is trying to say, "three L-L voltages that can form, as vectors, an equilateral triangle".
That is, three L-L voltages that are symmetrical.
mivey said:
. . .the positive, negative, and zero sequence vectors rotate counter-clockwise using the conventional layout.
Thanks.
You're right.
real world broken delta
...That's part of the real world to math transform jump that doesn't work...
Actually, the "broken delta" is a real work application used to measure 3V0. It is a set of PT secondaries connected in series. They have a safety ground on one end and the sum (the voltage to ground at the other end) is 3V0. This is referred to as a "broken delta". There is usually a zero sequence load added across these. I don't know where the L-L value that nisri had came from, but I supsect they came from a broken delta.
Obviously, the terminal readings of a delta transformer would not be broken but would be closed since the terminals are tied together. I think zero sequence can rotate in the delta, but we can't see it using the closed delta.
Here are some broken delta links:
http://pm.geindustrial.com/FAQ/Documents/750_760/GER-3182.pdf
(discussion on page 5, picture on page 8)
http://www.abbus.com/abbrelays/pdf/appdoc/AN-80D-01.pdf
(see page 2 & 3)
http://www.basler.com/downloads/pc-59n01.pdf
(nice picture of it in figure 2 on page 3)
http://www.selinc.com/techpprs/6161.pdf
(See figure 13 on page 10 and the discussion)
[edit: I guess using the term "L-L" voltage caused the confusion]
But the broken delta connection does not measure L-L voltages. As you say, it sums the line-to-ground voltages. The windings are secondaries of wye connected primary VTs.
Any measurement of L-L voltages that do not add to zero must be in error or taken at different times.
True enough. That's what made me think that the "L-L voltages" that nisri was referring to came from the readings across the broken delta coils, not the system L-L readings.
As I said, the term "L-L" may be causing the confusion. It would appear his "L-L" readings were coil "L-L" voltages. It's not completely clear in my mind yet.
If you can read these JPEGs, note the Physical Meaning starting at the bottom of the first image.