I'm trying to understand why grounding transformers are put on solar projects where the transformer is Yg-Yg. Is it due to the condition where the ground source is lost if the breaker at the local substation is tripped and the PV site is islanded with the distribution circuit until the PV site shuts down in 2 seconds or less due to islanding detection?
I'm working on a project where there is a zigzag transformer connected on the 600V side of the 23kv/600v Yg-Yg Transformer. The zigzag is fed from a 400A electronic breaker in a switchboard that shunt trips the 2500A MCB. Typically I see Yg - Delta grounding transformers on solar projects so this is a new one for me.
Wouldn't the grounding transformer, under steady state conditions, be a grounding source for the local distribution circuit for imbalances? The rating of the transformer is 867A continuous on the neutral. Is there an easy way to determine what conditions on the distribution circuit could trip the circuit breaker and dump the project?
I'm working on a project where there is a zigzag transformer connected on the 600V side of the 23kv/600v Yg-Yg Transformer. The zigzag is fed from a 400A electronic breaker in a switchboard that shunt trips the 2500A MCB. Typically I see Yg - Delta grounding transformers on solar projects so this is a new one for me.
Wouldn't the grounding transformer, under steady state conditions, be a grounding source for the local distribution circuit for imbalances? The rating of the transformer is 867A continuous on the neutral. Is there an easy way to determine what conditions on the distribution circuit could trip the circuit breaker and dump the project?