- Lockport, IL
- Retired Electrical Engineer
Re: Zinsco Mystery
What I am suggesting is another possible explanation: that the entire bus may be dead. Supposing that the 20/1 is off the other bus, and is working. What that means is that you have no loads that are powered by the failed side, and that you could turn on, in an effort to see if the bus itself has power. It could be a simple as a loose connection that was jostled during installation of the feeder to the range.
By any chance, is the 20/1 breaker feeding the receptacle powered from the same bus as the side of the 200/2 that has failed? If so, does it have power? When your electrician tested "all the wiring," did that test include the internals of the panel?Originally posted by hmspe: An electrician tested all the wiring in the house and found no problems or mis-wiring of any kind.
Actually, I think the most likely times for something to fail are when you turn it on for the very first time, and when you turn it on the first time after you have changed something.Originally posted by hmspe:. . . that just happened to pick an odd moment to fail.