As per 505(c)(1), crossing from class 1 zone 2 to an unclassified area, sealing fittings are required on the boundary (not more than 10 ft away), I read the exception and had an understanding that if the run is fully in threaded conduit system with no fittings or conduit bodies, the sealing fittings are not required? Is this correct.
If the run was direct buried, can we install the sealing fitting on the other end (the unclassified area side)?
Also, in exception 4 or 5 to this point, boxes containing splices or terminations were highlighted to be explosion proof (or this is the way I understood it), is the reason these being heat generation point if getting loose or open?
Best Regards