rcwilson
Senior Member
- Location
- Redmond, WA
Mike 01- We have used it on a couple of power plants' 600V switchgear. The latest has six double-ended lineups (main-tie-main) of Cutler-Hammer gear with 3200 A mains and many 1600A and 800 A feeders. Seems to be working Ok after a couple of installation issues were resolved where the signal wires were not connected across the shipping splits.
In previous employment, I commissioned two or three Square D 480V systems with full primary injection testing of the system with no issues.
I'm sold on it.