what will be acceptable to the ahj to conform to the 2011 nec to calculate aic per new 110.24
He says, the panel's comments clearly indicate their intention was for this label to contain the fault current value provided by the utility.
He says, the panel's comments clearly indicate their intention was for this label to contain the fault current value provided by the utility.
110.24 Available Fault Current.
(A) Field Marking. Service equipment in other than
dwelling units shall be legibly marked in the field with the
maximum available fault current. The field marking(s) shall
include the date the fault current calculation was performed
and be of sufficient durability to withstand the environment
involved.
(B) Modifications. When modifications to the electrical
installation occur that affect the maximum available fault
current at the service, the maximum available fault current
shall be verified or recalculated as necessary to ensure the
service equipment ratings are sufficient for the maximum
available fault current at the line terminals of the equipment.
The required field marking(s) in 110.24(A) shall be
adjusted to reflect the new level of maximum available
fault current.
Exception: The field marking requirements in 110.24(A)
and 110.24(B) shall not be required in industrial installations
where conditions of maintenance and supervision ensure
that only qualified persons service the equipment.
Now that bluesmoke has been kind enough to post the actual text, it is clear that the requirement is not related to the AIC. It has to do with the available fault current, not the capacity of the equipment to withstand a fault.. . . the 2011 nec (requirement) to calculate aic per new 110.24
If the utility provides the service transformer, they should be able to determine the fault current available at its secondary terminals. But if the utility service point is on the primary side of the transformer, then the owner will have to arrange for a calculation to be performed.He says, the panel's comments clearly indicate their intention was for this label to contain the fault current value provided by the utility.
Not at each panel, but only at the service panel.I read it to mean you just have to put the number your calc shows at each panel in your system.
There is already a requirement for field labeling (i.e., arc flash information), and this one applies to all panels, not just the service panel.Wow, field labeling now... another PITA.
Ask and you shall receive
But if the utility service point is on the primary side of the transformer, then the owner will have to arrange for a calculation to be performed.
Not at each panel, but only at the service panel.
The problem is still in getting a value from the utility. Most of the ones I have talked to will be providing their "maximum design level". This is the point they guarantee their system will never exceed and usually bears little to no relationship to what is currently available.
I also find the "Modifications" section interesting. How would anyone know there has been a (utility) modification that would affect the available fault(s).
This is a training issue.Exactly, and if used for an arc flash study could lead to false faster clearing times and lower Ei's than actual. Eventually, someone wearing the PPE listed on a label from these assumptions is going to get burned.
No.That could be an in house modification, like adding motors, but I have a hard time believing if the utility makes a modification they will inform everyone that is affected.
How many companies that allow unqualified persons to service the equipment will admit it and tell the installation contractor that labels are needed?Exception: The field marking requirements in 110.24(A) and 110.24(B) shall not be required in industrial installations where conditions of maintenance and supervision ensure that only qualified persons service the equipment.
Not at each panel, but only at the service panel.
This is a training issue.
Right now we deal with enough poorly trained people that try to perform AF calculations using the AIC rating of the equipment.
This label has one purpose in life. To make it easier for inspectors, and others, to verify compliance with 110.9 and 110.10. Any thing else is a misuse.