lakee911
Senior Member
- Location
- Columbus, OH
cause NEC says too
That is what I thought too... interesting discussion though...
cause NEC says too
That is what I thought too... interesting discussion though...
The first two are.What is a circuit conductor?
I know of ungrounded, grounded, and grounding conductors?
The first two are.
We nay-sayers believe that an EGC would have to carry normal circuit current, which it's not permitted to do, to be a circuit conductor.My opinion says a grounding wire is part of the circuit. May never be used but when it is it sure better be a conductor.
Agreed, and a jumper would have to be added. Fortunately, that does not apply when only the EGC is spliced.It did not say all of the conductors had to be spliced and often they are not. Soon as 1 is cut and spliced we now fall under the requirement to bond the box.
We nay-sayers believe that an EGC would have to carry normal circuit current, which it's not permitted to do, to be a circuit conductor.
Agreed, and a jumper would have to be added. Fortunately, that does not apply when only the EGC is spliced.
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
Where circuit conductors are spliced within a box ... any equipment grounding conductor(s) associated with those circuit conductors ...
250.118 Types of Equipment Grounding Conductors.
The equipment grounding conductor run with ... the circuit conductors ...
The bold sections taken from the respective posts certainly suggest that EGC's are not included in "circuit conductors."110.10 Circuit Impedance and Other Characteristics.
... between any circuit conductor and the grounding conductor ...
IMO it the EGC is never an 'NEC circuit conductor' under any condition.
As an EGC not a circuit conductor.
The circuit conductors, one hot and one grounded, are not spliced or terminated on equipment within the box, so even though the EGC's are spliced, there is no requirement under 250.148 to jumper or otherwise bond the EGC's to the box.
Look at that myself, Smart and Bob agreeing on something.
The first part of this article makes no sense. If the conduit is good enough to be considered an egc then why would you need to bond the box again simply because circuit conductors are spliced. Don't pull a ground wire and you don't have to do anything other than splice the circuit conductors.
Does anyone know the logic to this?
I have no problem with it, if you run an EGC they want you to use it.
I see no hardship or any reason to worry about it.
Definitions from 2008
Grounded Conductor--A system or Circuit conductor that is intentionally grounded
Grounding conductor--A conductor used to connect equipment to the grounded circuit of a wireing system to a grounding electrode or electrodes.
The words Circuit conductor are not used in the deffinition of Grounding conductor your honor. I rest my case.
I think most of us are in agreement with you Cavie.
Definitions from 2008
Grounded Conductor--A system or Circuit conductor that is intentionally grounded
Grounding conductor--A conductor used to connect equipment to the grounded circuit of a wireing system to a grounding electrode or electrodes.
The words Circuit conductor are not used in the deffinition of Grounding conductor your honor. I rest my case.
Interesting discussion. I always thought the likelihood of a fault would be increased because of the added termination or splice, or possible failure point. Therefore you would need additional bonding for reassurance.