I just had a disagreement with a friend of mine dealing with the allowable ampacity of a #14 thwn conductor to a 10 amp pool pump.I told him as long as the pump terminations were rated for 75 degrees and breaker was 75 degrees the phase wires could be #14 under a 20 amp breaker.He disagreed with me. I told him equip. grnding cond. had to be #12 but hot legs could be # 14 under these circumstances. Am I right?