Larry,
Don
That is very often the case and the reason why you must have a true available fault current value to do the arc flash calculations. If the available fault current is less, it may move into the short time trip range of the OCPD and not the instantaneous range. If there is a longer trip time with a lower fault current, the incident energy may very well be greater than a higher fault current that causes the OCPD to operate in it's instantaneous range.I am not very knowledgable in this area, but if what you are saying about IE is true; why wouldn't we need higher levels of protective gear at lower levels of available fault current instead of vice versa?
Don