mivey

Senior Member
...I do have a little bit of of a concern with the use of + and - signs on an alternating current source.
It was not like that in the original edition. Here is a page from my copy of the 1962 edition. I also find it interesting that Rick chose to crop off the remainder of the paragraph he quoted.

Hayt-Center-tap.jpg
 

Rick Christopherson

Senior Member
I have not once suggested that there is a phase shift. As Mivey said, there is no shifting going on.
Besoeker, I have been very patient with you for the past couple of days, but that patience has its limits when you keep flip-flopping in what you are saying. If you are unsure about your position, or are unable to communicate it using the English language, then you need to bow out of this discussion.

You have emphatically stated that you must have a 180? phase shift, but then deny making such a claim. You have affirmed that a phase shift is a time shift, but then later deny that. You've agreed with my previous assertions, but then later deny it.

I cannot carry on a discussion with someone that doesn't even know what their own position is about. If you don't understand what your position is, or can't decide what position you want to take, then leave the discussion to those that do understand.

Yes, I do have an answer for how neutral currents cancel, but we can't even get there until you figure out what your position is. It's a moving target, but if you sit still, I will hit it.
 

Rick Christopherson

Senior Member
I also find it interesting that Rick chose to crop off the remainder of the paragraph he quoted.
If you are suggesting that I lied, then state it! If you are suggesting that there was some information shown after my quote that I deliberately hid, then state it!

Don't pull this innuendo B.S. and suggest I did something inappropriate, but then fail to say what it was. If you can't substantiate your innuendo, then it just goes to show what dishonest lengths you will go to in an attempt to make a point. Can you substantiate your innuendo?
 

mivey

Senior Member
I note also, that you have not come up with an alternative and credible explanation of why the neutral currents cancel that negates the obvious that they are displaced by 180deg.
I suspect it is because he can't. I find it incredible that a EE would deny that the voltages are displaced by 180?. That fact is used in so many places in our field it just boggles the mind.

Here is a quote from your side of the pond from Prof. G.W. Carter of the University of Leeds in his 1972 "Techniques of Circuit Analysis" (I hit the color button on my scanner for the second page but did not feel like re-doing it):

Carter-TOCA-Center-tap.jpg
 

mivey

Senior Member
If you are suggesting that I lied, then state it!
I do not think you lied. It was not meant to be as dramatic as you are taking it.

If you are suggesting that there was some information shown after my quote that I deliberately hid, then state it!
I think you deliberately left off the rest of the paragraph.

Don't pull this innuendo B.S. and suggest I did something inappropriate, but then fail to say what it was. If you can't substantiate your innuendo, then it just goes to show what dishonest lengths you will go to in an attempt to make a point. Can you substantiate your innuendo?
I'm not saying it was inappropriate as we are not talking about defending a murder rap. :D

I just think leaving off the other part was self-serving. Can't say I really blame you as you are under no obligation to present information that does not help your position. Interesting nonetheless.
 

mivey

Senior Member
Besoeker, I have been very patient with you for the past couple of days, but that patience has its limits when you keep flip-flopping in what you are saying. If you are unsure about your position, or are unable to communicate it using the English language, then you need to bow out of this discussion.
It would help if you would actually read his posts without trying to read into his posts.

You have emphatically stated that you must have a 180? phase shift
Please post the quote as I must have missed that.

...but then deny making such a claim. You have affirmed that a phase shift is a time shift, but then later deny that. You've agreed with my previous assertions, but then later deny it.
As far as I can tell, you are not reading what he is writing.

I cannot carry on a discussion with someone that doesn't even know what their own position is about. If you don't understand what your position is, or can't decide what position you want to take, then leave the discussion to those that do understand.
Do you find that this communication method works for you in other areas? It is not a productive way to have a discussion. I have been around the block a few times and can tell you that most professionals I have met have very little respect for people who communicate that way. Whatever floats your boat I guess.

Yes, I do have an answer for how neutral currents cancel, but we can't even get there until you figure out what your position is. It's a moving target, but if you sit still, I will hit it.
I'm on the edge of my seat. :sleep:
 

Rick Christopherson

Senior Member
I think you deliberately left off the rest of the paragraph.

I'm not saying it was inappropriate as we are not talking about defending a murder rap. :D

I just think leaving off the other part was self-serving. Can't say I really blame you as you are under no obligation to present information that does not help your position. Interesting nonetheless.
It wasn't included because it neither applied to nor refuted what I stated. You quoted the remainder of the text, so there is no secret about its contents. I gave a full bibliographical reference specifically so someone like you could not claim I misquoted.

I find it absolutely unconscionable that you would suggest I stopped my quotation because I was trying to hide something--especially when your re-quotation of the same text specifically reveals that I wasn't hiding anything.

You made the innuendo that I tried to hide something, yet you haven't, and can't, explain to anyone what it was that I was trying to hide! That is very poor form, and highly dishonest on your part.
 

Rick Christopherson

Senior Member
It was not like that in the original edition. Here is a page from my copy of the 1962 edition.
This comment did not slip past my purview. This may result in a warning from our moderator (and I apologize in advance), but I find it quite interesting that the only major participants battling against this discussion are those that have been in the business for 40, 50, 60 years, and their ways are so set that they cannot fathom allowing someone else to view a system different from themselves.

Are you really arguing because this information is wrong, or because you have to have everyone do things your way?
 

mivey

Senior Member
This comment did not slip past my purview. This may result in a warning from our moderator (and I apologize in advance), but I find it quite interesting that the only major participants battling against this discussion are those that have been in the business for 40, 50, 60 years, and their ways are so set that they cannot fathom allowing someone else to view a system different from themselves.

Are you really arguing because this information is wrong, or because you have to have everyone do things your way?
Bes commented about the use of + and - symbols on the diagram. That was not they way the author originally drew it so he either changed his preference over the years or it was changed by the editor or publisher.
As for the rest of your post: :?
 

hurk27

Senior Member
What I am having a hard time understanding is those who refuse to accept that a center tapped transformer can have these secondary windings paralleled to only provide 120 volts, now if these two sections of windings were 180? out of phase I do not think this would work.
Second in both posted books they both say that these two windings "being equal must have the same phase angle" but does say that "from another "view point" the voltages from the center (neutral) and the outer wires are 180? out of phase, so if this is a view point then it is using a instrument to view this wave being that would be an oscilloscope would make sense since the common input could only be connected to the center wire and then each red lead would connect to each end wire, this connection will have one red at A common at N and the other trace input red at B with will put B trace 180? out from A we should know that we have A+ A-N for the first 1/2 of the winding then B+N then B- for the second winding so if we look at our trace leads on B they are in reverse polarity with B's winding, this is where we are getting the 180? out of phase from????

does a winding jump 180? out of phase when you put a center tap on it? only if you reference the center tap with both black leads to the scope, this is the same with two batteries, +-+- the connection between the two batteries is common but not the same polarity with the other two ends and to properly read each battery you will have to place the red lead where there is a + sign and the black lead where there is the - sign this will cause a red and black lead on the common.

In both of the above the only thing out of phase is the "view point" not the windings or the batteries.

Oh by the way a DC Edison circuit with two batteries and a common connection will also have no common current when two identical loads are placed from this common to each end
 
Last edited:

templdl

Senior Member
Location
Wisconsin
It is of my opinion that there may not be a big difference between a 120 and a 240v motor when their running but I believe that the starting torque would be greater for the 240v motor because there would be less voltage drop at that time.
 

mivey

Senior Member
Here are some more quotes :

"Center-Tapped Transformer and 120-/240-V Secondary Models" William H. Kersting:
Distribution engineers have treated the standard ?single-phase? distribution transformer connection as single phase because, from the primary side of the transformer, these connections are single phase and, in the case of standard rural distribution, single phase line to ground. However, with the advent of detailed circuit modeling, we are beginning to see distribution modeling and analysis being accomplished past the transformer to the secondary, which now brings into focus the reality that standard 120-/240-V secondary systems are not single-phase line-to-ground systems, but they are three-wire systems with two phases and one ground wire. Furthermore, the standard 120-/240-V secondary system is different from the two-phase primary system in that the secondary phases are separated by 180? instead of three phases separated by 120?.

"Handbook for Electrical Engineers" 1917, Harold Pender:
Strictly, the so-called single-phase system is a star-connected two-phase system, since the currents from the two terminals are in opposite directions at any instant, the current leaving by one and entering by the other. However, in practice the name two-phase system is used for a system supplied from a generator or other source of e.m.f. having two windings in which are developed two e.m.f.'s differing in phase by 90?; i.e., a two-phase system is in reality two distinct single-phase systems each with two terminals.

"M-I-C-K-E-Wye" Richard P. Bingham, Dranetz-BMI:
A "delta" circuit looks like the delta symbol, which is an equal-sided triangle. There are numerous variations of the delta circuit, such as: grounded deltas (one corner of the triangle is connected to a grounded conductor); open-leg delta (only two elements instead of three are used); or, crazy-leg (where one leg is center-tapped to produce two voltages that 180 degrees out of phase from each other).

"Navy Electricity and Electronics Training Series-Module 8?Introduction to Amplifiers-NAVEDTRA 14180 pg 1-7":
One way in which a phase splitter can be made is to use a center-tapped transformer. As you may remember from your study of transformers, when the transformer secondary winding is center-tapped, two equal amplitude signals are produced. These signals will be 180? out of phase with each other. So a transformer with a center-tapped secondary fulfills the definition of a phase splitter.

"Photovoltaic Power Systems and The National Electrical Code", Sandia National Laboratories:
In a utility connected system or with a 120/240-volt stacked pair of inverters, where the 120 /240-volt power consists of two 120-volt lines that are 180 degrees out of phase, the currents in the common neutral in the multiwire branch circuit are limited to the difference currents from any unbalanced load. If the loads on each of the separate branch circuits were equal, then the currents in the common neutral would be zero.

I also have many quotes dealing with baluns and how the fact that the neutral-referenced signals are displaced by 180? is used to link unbalanced circuits with balanced circuits. Most have pictures but I am getting tired of logging into Photobucket so here is just one (from a lecture by Dr. Charles Baylis, Ph.D at USF covering baluns):
Baylis-Center-tap.jpg
 

Rick Christopherson

Senior Member
What I am having a hard time understanding.....
And your confusion is exactly why I am willing to risk my personal reputation on this topic to resolve this in light of some very adverse opposition.

I am not the only person from this forum that opposes the misinformation that is being presented in this discussion, but I am apparently the only one willing to risk my reputation to stand up to it. I have taken a lot of hits for it, but it should be becoming clearer and clearer that these hits are less and less reputable.

I have been called a fool for going toe-to-toe with the "old boy's club", but if you pay attention to the discussion, you will note the complete absence of any information proving me wrong. To the contrary, what I state is supported by engineering text, yet the old-boys wish to dismiss this as tricks from the editor.

I am not foolish enough to think that I can teach the "ol' boys" that they are wrong, but I can at least make sure that other people are well informed as they make their own decisions.
 

hurk27

Senior Member
Mivey:

I noticed that you keep referring to transformers appear to be fed from the Polly phase supply where you would still have reference to the 120? phase shift between the phases, this is where and only where you can use an open Y bank from 2 phase conductors and the neutral to create a 3 phase output from the transformer bank, after you have transformed through a single phase transformer you no longer have this option or we would never need roto phase converters, some of the references also would not apply after you have transformed through a single phase transformer, and in a building with only 240/120 single phase as this has already been done.

if I have this wrong someone educate me:happyyes: this is how I learn:thumbsup:
 

mivey

Senior Member
What I am having a hard time understanding is those who refuse to accept that a center tapped transformer can have these secondary windings paralleled to only provide 120 volts, now if these two sections of windings were 180? out of phase I do not think this would work.
Who has refused to accept that? I have said more than once that both configurations are valid.

Second in both posted books they both say that these two windings "being equal must have the same phase angle" but does say that "from another "view point" the voltages from the center (neutral) and the outer wires are 180? out of phase, so if this is a view point then it is using a instrument to view this wave being that would be an oscilloscope would make sense since the common input could only be connected to the center wire and then each red lead would connect to each end wire, this connection will have one red at A common at N and the other trace input red at B with will put B trace 180? out from A we should know that we have A+ A-N for the first 1/2 of the winding then B+N then B- for the second winding so if we look at our trace leads on B they are in reverse polarity with B's winding, this is where we are getting the 180? out of phase from????

does a winding jump 180? out of phase when you put a center tap on it?
We can take an EMF to be in either direction. It is "jumping" at regular intervals and there is nothing that says jumping in one direction is anymore correct than jumping in the other. The source configuration does not completely define how we have to take the voltages from it. Please refer to some of the other information I have posted.

only if you reference the center tap with both black leads to the scope, this is the same with two batteries, +-+- the connection between the two batteries is common but not the same polarity with the other two ends and to properly read each battery you will have to place the red lead where there is a + sign and the black lead where there is the - sign this will cause a red and black lead on the common.

In both of the above the only thing out of phase is the "view point" not the windings or the batteries.
Please refer to the other information I have posted and you will see that the voltages are real forces that can produce real work and are not just viewpoints.

Oh by the way a DC Edison circuit with two batteries and a common connection will also have no common current when two identical loads are placed from this common to each end
No one has suggested hooking up the voltages such that they are in opposition. They are hooked up in a manner such that they work in concert. Follow my post #98 and that should become clear to you.
 
And your confusion is exactly why I am willing to risk my personal reputation on this topic to resolve this in light of some very adverse opposition.

I am not the only person from this forum that opposes the misinformation that is being presented in this discussion, but I am apparently the only one willing to risk my reputation to stand up to it. I have taken a lot of hits for it, but it should be becoming clearer and clearer that these hits are less and less reputable.

I have been called a fool for going toe-to-toe with the "old boy's club", but if you pay attention to the discussion, you will note the complete absence of any information proving me wrong. To the contrary, what I state is supported by engineering text, yet the old-boys wish to dismiss this as tricks from the editor.

I am not foolish enough to think that I can teach the "ol' boys" that they are wrong, but I can at least make sure that other people are well informed as they make their own decisions.

As steps Don Quixote bravely forward on his stately Rocinante to battle the ferocious Giants disguised as windmills. Chivalry will surely win the day, just by the sheer veracity of our Brave and will receive his just rewards on the bosom of the lovely Dulcinea.
 

hurk27

Senior Member
Baylis-Center-tap.jpg

Ok in the above diagram of a single phase transformer with two secondaries that are connected together at center point we can notice the polarity dots, so with this in mind if I connected a dual trace scope in this manner trace 1 input = red to 3 black to 4 trace 2 input red to 5 black to 6 I should get two identical wave forms that will trace in the same path across the screen in step with each other and positive at the same time and visa versa, I would try this but I would have to use an input isolator for my quad trace as the inputs are common on the shield and I don't have an isolator.
 