The other day I was troubleshooting some pole lights, found this inside, this is tied into a lighting control panel to turn the lights on in case of an emergency. Not sure if this is allowed, I was unable to find anything other than clearance issues. This is a 480v single phase pole light, 3 pole contactor with 277v coil. Switch is 3 pole manual motor starter that operates lights until 11pm, during an emergency relay in LCP sends 277v to coil on contactor. There are other obvious issues here, just want to know if mounting contactor inside hand hole is allowed.