ElectricianJeff said:
When I went to finish today I elected to just pig-tail the 4 neutrals in each recep. since I didn't think it really would matter as to the operation of the 3-way.
Neutrals of this size cannot be in parallel. The extra wire should be left unused OR the tab needs to be removed from both sides of the receptacle.
Mark
quogueelectric
new york
3way
3way
as far as the 3 way you need 3 parts #1 a feed..........#2 travellers..........#3 a load or switched leg... You did run a 3 wire between 3 way switches and the easiest way is to feed at 1st switch 3 wire travellers to 2nd switch and switched load to devices or lights. Sounds to me like you forgot your travelers between switches.
480sparky
Iowegia
Jeff: Are you saying you ran 12/4 from the first 3-way to a split recep, then over to the other three-way? Like this?:
3-way-------recep----------recep--------recep-------------3-way
If you did, you won't be able to make the 3-ways work a split recep. You will need a total of 5 conductors, one hot, two travellers, one switch leg and the neutral.
You keep talking about the neutral and extra neutrals and splitting the neutral side. The neutral has nothing to do with 3-way switching and split receps.... it's all done on the hot conductors.
charlie tuna
Florida
not enough information
your post does not give a full picture of what you did!! anyway you do it, the neutrals can be separate or common to all the receptacles provided they are spliced together if common???? you need a feed or hot into one three way and two travelers to the other three way, and a switchleg from that three way back to the switched conductor connected to the switched side of the receptacle. you also must have a hot to the unswitched side of the receptacles. easy.................... now what did you do wrong??
Chenley
Western KY
This is the only two ways I have to wire them:
Sorry about the background. Would have it on white except it would color the neutrals black and :confused: people.
al hildenbrand
Minnesota
Electrical Contractor, Electrical Consultant, Electrical Engineer
Take a look at using the "Traveling Bus 3 way" to make this work.
ElectricianJeff
Sorry....had my monthly poker club last night and wasn't able to stay on top of this thread but I did win some $$$. I am truly amazed by the number of responses.
Heres what I did at rough in:
3way---12/2/2---recep---12/2/2---recep---12/2/2---recep---12/2/2---3way
12/3 3way to 3way
I have the line at one 3 way and the recep load at the other.
Right or wrong, I elected to pig all neutrals (4 total) at each recep making a common neutral for each.
I am headed back there Thurs. so any help making this work is obviouslly greatly appreciated.
Jeff
cadpoint
Durham, NC
Just Bold
Just Bold
Let me back of my earlier statement of Forward or Aft ...
I've never seen that, nor every applied that, that is to Cool.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Jeff-what about conductor fill in that 3 way. Power 12/2 plus 12/3 for 3 way wires plus 12/2/2--- that's 10 conductors without the device or clamps.
I also see issues with parallel neutrals.
Dennis Alwon
Chapel Hill, NC
You really don't need the wire from the last recep. to the 3 way switch.
Just dead end one 3 way ( don't use the 12/2/2 from the second 3 way to the recep) and have feed and switched wires come from the first 3 way switch to the first rec. Don't use the second neutral in the 12/2/2 that feeds the recep.
benmin
Maine
Master Electrician
12/3 3way to 3way
Jeff
Sounds like you might just have a switch miswired. I would check them first.
Feed 3way: 1. All neutrals tied together and stuffed into back of box 2. Red from 12-2-2 capped and stuffed into back of box. 3. Black from 12-2-2 and black from feed tied together and connected to the switch leg screw of the switch (black colored). 4. red and black from the 12-3 used as travellers.
Load 3way: 1. All neutrals tied together and stuffed into back of box. 2. Black from 12-2-2 capped and stuffed into back of box. 3. Red from 12-2-2 connected to switch leg screw on switch (black colored). 4. red and black from the 12-3 used as travellers.
The most common mistake I find is when on the 3way at load side, The Black (always hot) is connected to the 3 way instead of the red (switched)
Dennis Alwon
Chapel Hill, NC
This is an illegal hookup with all whites tied together-- art 310.4
benmin
Maine
Master Electrician
OK. Then we can disconnect the 12-2-2 red/white in the feed 3way, cap it and place in back of box. That way it will not be "electrically joined at each end"
Dennis Alwon
Chapel Hill, NC
You would have to disconnect the red striped white wire everywhere. It still is feeding as a loop from the other direction.
R2006
PENNSYLVANIA
Hi Jeff.
Not sure if i understand the question but I'll give it a try.
You have a hot at one 3-way, then you need 3-wire looping the affected outlets, and a 3-wire to the other 3-way, at the 3-way with the hot, splice the nuetral and the white going to the outlets, splice the hot and the black going to the outlets with the black going to the other 3-way, (or what ever color you prefer) the 2 remaining wires to the other 3-way become your travlers,on the 3- way with the hot you should have a red and white to the other 3-way they go under the common screws and the red to the outlets under the diffrent screw, at the outlet break the hot tab(dont break the neutral) and at the other 3-way red and white under common screws and black under diffrent screw. double check me it's been a busy day but i think this should work for you.
al hildenbrand
Minnesota
12/3 3way to 3way
Jeff,
It'll be simpler with lower wire count to ditch the 12/3.
benmin
Maine
Master Electrician
Even though I believe it is redundant wiring, You're right by my understanding of 310.4:mad:
fisherelectric
Northern Va
Why not just feed it in the receptacle, run a 2-wire switch leg to the first three-way, a 3 wire between switches. Then if you want more 1/2 hot receptacles , come from the first receptacle to the others with a 3 wire.