I figure y'all are the right people to ask. Not that you've ever been asked this before, but because I'm sure this will be an interesting discussion.
We have a growing amount of 50Hz 230 volt power (single phase of a 230/400 volt system) that's being produced at the office. Right now it is all being turned into heat courtesy of a rather large dump load.
The way things are wired right now, there is a several KW 50Hz power supply that is providing a grid reference to what I think is a 2 or 3KW solar array that is powering 50Hz microinverters. The microinverters are back-feeding the supply, which has its output paralleled with the dump load. So, if the sun isn't shining, the dump load is turning most of that 50Hz power into heat. And if the sun is shining, even more of it is turned into heat.
What are the code issues that might be associated with actually =doing= something useful with that power?
You should be able to experimentally run 265v rated PTAC heat-pump(designed to run on 277v single phase circuit) . It would be a great exercise to see if the inverter can handle the rigor of motor starting.
Since 277/60 = 4.61 and 230/50 = 4.6, the motor gets a good V/Hz match. The BTU capacity would be reduced because compressor slows down. If the RTC(timer) on the unit uses line frequency, then, that function would be useless, because it would clock every hour as 5/6 of an hour.
Japanese spec refrigeration equipment are often 50/60Hz rated, but have two BTU ratings, one for 50Hz, one for 60Hz. Capacity is reduced at 50Hz for the aforementioned reason.
If the PTAC is setup like a window A/C and connected with cordsets, it would be laboratory test load that happens to need access to outdoor air.