RayS said:
the ammeter connected to the conductive body would read higher, as it (the body) is now a much larger "sink" than the dangling wire.
Hey Ray, :smile:
Your specualtion above is the same speculation we were arguing over in the "current returning to a different source" thread. Please allow me to give my thoughts and I certainly welcome your return comments. (note to moderators: I am being civil and am in no way demeaning Ray for his thoughts)
Your proposed principle above leads to some absurdities. For example, I am taking that you say "the larger the sink" the larger the current flow.
Absurdity 1) Given: Experiment in outer space, Conductive body connected to one side of AC source, dangling wire on the other side of AC source: If current increases for the larger conductive body or "sink", then if we start using larger and larger conductive bodies, then we will have larger and larger current flows to the conductive body. What if the conductive body is the earth itself? How much current would flow to and from the earth? it should be quite a large amount, right? Thousands of amps possibly? Well, we know that isn't true because there are thousands of grounded phase deltas working right now as we speak. And there is no large current flow from the phase to the huge "sink" of the earth.
Absurdity 2) Given: Experiment in outer space, Conductive body connected to one side of AC source, dangling wire on the other side of AC source: Say we have the means to connect a conductive body to the AC source only for the first quarter cycle. Current will be flowing to the conductive body and it will be gaining electrons.
At the peak of the first quarter cycle, we remove the conductive body from the circuit. We have trapped the excess electrons on the body. Then we take a new conductive body and do the same thing in the first quarter cycle. More electrons removed from the AC source. Now repeat over and over with new conductive bodies. Pretty soon, we will have deleted ALL of the electrons in the source. I am pretty sure that this is impossible.
One thing we can't forget. When we speak of voltage sources, however many electrons are flowing out of the negative terminal of the source, there must be the same number of electrons entering the positive terminal of the source. This is basic physics. (Of course, something wild like a lightning strike to one terminal of the source may violate the rule, but that is way beyond and is definitely not what we are talking about)
So if we are moving electrons to the conductive body during the first quarter cycle, we are also pulling electrons out of the dangling wire. The amount of electrons moving to the conductive body will be the same exact amount that we pull out of the dangling wire. The dangling wire will become positive. And since the conductive body is negative, there is an electric field between the conductive body and the dangling wire. This electric field created by the source voltage is what allows electrons to flow onto the conductive body. It all works hand in hand. The conductive body can only accept as many electrons as the positive side of the circuit will allow. And the ammeters will always read the same. (again, we are talking theoretical experiments here, so things like resistance of the air, electrons flowing through the air around the meters and such are not what we are talking about. All of those things can be accounted for by basic electricity and resistors and ohm's law)
It is the capacitance of the dangling wire to the conductive body that determines the amount of current flow to the conductive body. Again, it is the
capacitance of one body to the other that is what matters.
If we were to increase the area of the dangling wire, then you would notice the current to the conductive body going up. But both meters would read exactly the same.
Summing up: If you have a voltage source such as a xfmr secondary, and if electrons are pushed out of one terminal and cause a particular conductive body to become negative, then I can show you another conductive body that has become positive by the same exact amount.
Even with a conductive body connected to terminal X1 of a secondary and nothing connected to the X2 terminal, the same thing will still happen. If Terminal X1 sends electrons to the conductive body, Terminal X2 itself will become equally and oppositely charged (positive) compared to the conductive body. This is capacitance and the physicists have defined capacitance to account for the very observations of the experiments. There is not other "mystery force" that allows current to flow other than capacitance, resistance, and inductance, and these items are well understood and documented.
Conclusion: The amount of current flow from a given voltage source to an isolated conductive body is not determined solely by the characteristics of the conductive body. It is also determined by the characteristics of whatever conductive body is connected to the opposite terminal of the voltage source and the distance betwen the two bodies. . And these characteristics of the conductive bodies and distance between them is capacitance.