iwire said:Sure would like to see some documentation on this as I agree with David's post that "Smoke Alarms" (the proper UL classification of the line volt detectors used in homes) are not power limited fire alarm systems.
iwire, you are correct the hardwired smoke alarms found in residential construction are not considered power limited fire alarm systems, but are instead considered Non-Power-Limited Fire Alarm (NPLFA) Circuits as covered under Article 760 part II beginning with 760.21 and ending with 760.40(4). In contrast a Power-Limited Fire Alarm (PLFA) Circuit would begin with a panel supplied by a PLFA or Class 3 transformer (as defined in 760.41(A), in addition any smoke/fire detection system powerd such that it meets any of the following conditions is considered a Power-Limited Fire Alarm Circuit: 760.41(A), 760.41(B), or 760.41(C) as referenced by 760.2 and 760.41)
The power supply for PLFA circuits (meeting one of 760.41 (A) - (C)) are further defined in 725.41 (A) (1-4) using Tables 11(A) and 11(B), or Tables 12(A) and 12(B) respectively).
In particular, the Kidde (R) alarms, of which I am installing, are UL listed as 110v class 2 transformer powered with battery backup and in NEC 2005 760.24 after Exc 3 reads as follows:
FPN: A single-phase, listed electronic power supply whose output supplies a 2-wire (single-voltage) circuit is an example of a non-power-limited power source that meets the requirements of 760.21.
As such the installation of these particular Kidde (R) smoke detectors falls under the pervue of Article 760 section II.