It is explicit in the description of some AFCI operations that "parallel arc" tripping uses what is *effectively* a low mag trip which is only active when an arc signature is detected at the same time. Not sure what the unconditional mag trip level is.

Its said to be 75amps. At least (supposedly) this is the lowest short circuit current one can find in a resi home.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
The UL standards are consensus standards and developed in much the same way as the NEC is. There is a method to submit proposed changes to the standards, but I don't know exactly what that method is. I am sure is it on their web site somewhere.

I don't think the NEC had any AFCI requirements prior to there being a standard for the manufacturers to build the AFCI device to.

So UL1699 is what came first?
 

kwired

Electron manager
Location
NE Nebraska
I thought I saw a proposal where he sent in asking for GFP to be mandated in AFCIs.

But the CMP would be correct to reject such a proposal as that really belongs in the AFCI standard, not in the NEC, but I don't recall a proposal from him on that issue.

The way I understand it, manufacturers invented the AFCI and needed a standard to have it listed. So 1699 came into being after the invention of the product. The standard did not proceed the product.

Sort of makes sense, how do you have a standard for something that doesn't yet exist?

Does UL already have listing standards for warp drives?:cool:
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
The way I understand it, manufacturers invented the AFCI and needed a standard to have it listed. So 1699 came into being after the invention of the product. The standard did not proceed the product.


The original nema afci task force admitted defeat , when they did UL was asked to create a standard for the product Vs. testing a product to a standard.

To my understanding (which is nothing stellar) of UL , this isn't the norm.

~RJ~
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The original nema afci task force admitted defeat , when they did UL was asked to create a standard for the product Vs. testing a product to a standard.

To my understanding (which is nothing stellar) of UL , this isn't the norm.

~RJ~
Actually that is the norm....UL does and always has created standards. They are an ANSI standards creating agency just like the NFPA (and NEMA) is. They use a consensus method to create their standards as required by the ANSI rules. Their STPs (standard technical panels) are made up of representatives of different groups much like a CPM for the NEC.
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
Perhaps i'm not saying this right Don?

I was under the impression that any given manufactures claims were tested via NRTL's as to what it can /can not do, vs. the other way 'round...

~RJ~
 