Code wise, do you see any issues with this wiring?
IMG_6858.jpg
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Yea many..
Is that a swiches in the floor I see.......
Looks nice other than no protection for the NM
 

mdshunk

Senior Member
Location
Right here.
Nope. Looks like it closely follows the structure. If you failed me for that, I'd re-do it as open wiring on insulators on the ceiling and make you like it.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
My eye's playin tricks .. For some rediculous reason I was looking at it sideways.


OPP's
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
scwirenut said:
that is for type AC cable, nm does not have that limitation
Read art 334.23-- it applies to nm also.

That being said I have never seen an installation as such get turned down. I cannot imagine why that would be a violation.
 

scwirenut

Senior Member
Dennis Alwon said:
Read art 334.23-- it applies to nm also.

That being said I have never seen an installation as such get turned down. I cannot imagine why that would be a violation.


wow!. this is why I shop here, lol I have wired 100's of houses wrong..omg

you live and learn, thanks.....
 

quogueelectric

Senior Member
Location
new york
Pierre C Belarge said:
Code wise, do you see any issues with this wiring?
IMG_6858.jpg
I dont particularly like the wire being surfacemounted I do not see the service light , service receptacle or the service disconnect. I think the flue pipe has too many elbows in it but that is a plumbing issue I am not sure if it is a y or a t it should be a y.
 
Last edited:

M. D.

Senior Member
mdshunk said:
But it could have had a scuttle hole and not stairs.

Not sure that matters in regard to a wiring method

Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building

I don't think that wiring is permanently closed in even with a scuttle hole
 
Dennis Alwon said:
Read art 334.23-- it applies to nm also.

That being said I have never seen an installation as such get turned down. I cannot imagine why that would be a violation.


Just because a job may pass inspections in the area where you work, and the NEC is not being enforced does not make it a code compliant installation. (disregarding local codes)
It is a violation as per the section I presented.
And yes, there are many installations like this in the area I inspect in...that is until I see the job and speak to the EC. :wink: :D

MD
The wiring method is different for accessible attics by stairs, and attics that may be accessible by a scuttle hole...the difference is significant. Read all of 334.23- 320.23.
 

480sparky

Senior Member
Location
Iowegia
ItsHot said:
Yeah, You never know when the HO will be walking on his walls!:grin:

Or having the HVAC equipment replaced, or moving the ducts around during a remodel, or storing stuff against the walls, or using the NM to hang stuff off of......
 

ItsHot

Senior Member
code violation

code violation

Pierre C Belarge said:
Actually the issue is one of storage. When one gets into some of the attics, there is so much storage that the possibility of damaging the cables/conductors becomes significant.
Pierre I agree with your point! This may be one:-? of the most violated articles in residential wiring. I remember the most recent attic that I have been in. It had a drop ladder access without any "running board" protection. And a ton of stowables up there!
 