In order to run two 3/4" conduits in/out from 2"x4" back box of duplex receptacles, do we need to extend the size of back box?
infinity
New Jersey
Journeyman Electrician
What's a 2"X4" back box? One of these?
images
m sleem
Usa
Health
From the attached image i can see #6 opens in addition to #2 opens are hidden, does it mean no need to extend?
infinity
New Jersey
The box in the photo has 11 KO's, that number is irrelevant. According to T314.16(A) for a 4" X 2 1/8" X 2 1/8" deep you could install 6-#12 or 7-#14 conductors.
kwired
Electron manager
NE Nebraska
Outside of physical size and restrictions that naturally come up because of it - number of conductors filling the box are generally going to be your limitations. It is possible to enter the box pictured with too many conductors from just a single 1/2 inch raceway.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
They do make deep handy boxes that are 2 1/8" deep. Again as others have said it has nothing to do with the conduit size but rather on the number of conductors.
kwired
Electron manager
NE Nebraska
Those are easily overfilled with the capacity of just a single 1/2 inch raceway entry as well.
If you plan to have full raceways, you will need boxes with volume for the conductors. Handy boxes are only intended for the associated conductors of the installed device and have no volume for much anything else.