If you were an inspector how would you call this one? Bath tub is to the right. And if you had to move the receptacle where would you put it?
My first picture I hope it works.
Put the receptical in the mirror. It is done everyday.mistermudd said:
If you were an inspector how would you call this one? Bath tub is to the right. And if you had to move the receptacle where would you put it?
My first picture I hope it works.
Hi Mrmudd,mistermudd said:
If you were an inspector how would you call this one? Bath tub is to the right. And if you had to move the receptacle where would you put it?
My first picture I hope it works.
Cavie said:Put the receptical in the mirror. It is done everyday.
On the left side of the sink of course!!mistermudd said:
If you were an inspector how would you call this one? Bath tub is to the right. And if you had to move the receptacle where would you put it?
My first picture I hope it works.
Pierre C Belarge said:I am curious.
I see that the receptacle is not a GFCI device. Are there 2 sinks there, with one GFCI protected device by that other sink?
If not, is this a GFCI CBer protected device?
acrwc10 said:How could moving the outlet 5 inch's to the left into the mirror going to make it any safer ????????????????
If it is GFI protected I don't see a problem.
frizbeedog said:Good Point.
Yep, that's what it says and moving it 5" would make it code compliant, but... it still won't be one bit safer.gndrod said:Pierre's spot on. 406.8(C) Bathtub and shower space....Recepts shall not be installed within or directly over a bathtub or shower stall.
gndrod said:Pierre's spot on. 406.8(C) Bathtub and shower space....Recepts shall not be installed within or directly over a bathtub or shower stall.
acrwc10 said:This is one of those situations where your inspector can show you just how much of a power trip he needs or doesn't need to have. This is not a tub "stall" if you look at the receptacle it is over the tub "platform" as this is on a granite slab , and it is outside of the outer rim of the tub, if the counter was 3'' longer it would be over the counter.
90.1 Purpose.
(A) Practical Safeguarding. The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity.
(B) Adequacy. This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance results in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.
If the purpose of the code is safety and moving the receptacle doesn't make it "SAFER" why would you go to the letter of the code and not the purpose of the code??????????????????????