No, the whatever-length of the 2-0 will drop the voltage that that length of 2-0 will at the actual load current, and the 6" of #2 will drop the voltage that 6" of #2 wil at the same current. The current causes the voltage drop.If you need to upsize the wire to 2/0 for the run because of its length, it is OK to reduce the size of the conductor for that six inches or so near the breaker? Is there less current flowing through the conductor near the breaker?
Only if the breaker were sized larger than that required to protect the smaller wire.So your saying by reducing the wire size with a splice you would be in violation interesting.
The relative resistances are not relevant at all. What matters is that the smallest wire is protected.As long as the resistance of that 6 inches of smaller wire is less than the resistance of that whole run of 2/0, it doesn't matter.
Same here, but I do believe that form follows function, not the other way around. Make splices when you need to, just do them well first and pretty second.Generally I try to avoid any splices in a panel, I think they look tacky and unprofessional. When I do a panel I like to leave it looking like a work of art.
First, you should get no static because this is compliant, done correctly. Consistency comes from communication and accurate code understanding. There are proper channels for challenging what you believe to be an improper ruling.I'm just wondering if I'm going to get any static from an inspector about it. It's been my experience that when it comes to dealing with any government officials you are at the mercy of their individual personalities with practically no consistency from one to the next.
I'm sure we've covered that by now.I just thought I would try to get a general consensus of what's acceptable or prohibited in this situation.
Electrically, none, let's say. Legally, lots. Plus, it sure looks more unprofessional than splicing or pins.Im not sure what is the difference between trimming the wire and putting a splice in your reducing the wire size to fit the lug .
This is similar to the mixed-wire-size discussion we had over the last couple of weeks.
If the larger wire is used because of voltage drop and your reducing that wire size with a splice of some sort so it will fit in the lug are you not creating a problem by doing this or because of the short distance of the splice this will not affect the voltage
The latter. The smaller size was adequate before the voltage-drop compensation was used, n'est pas?If the larger wire is used because of voltage drop and your reducing that wire size with a splice of some sort so it will fit in the lug are you not creating a problem by doing this or because of the short distance of the splice this will not affect the voltage
I believe we're all in agreement. This says it all:You missed what I was saying. AV ELECTRIC and infinity are speaking about my point in the post above mine.
It's true that the relative location of each segment of the circuit doesn't matter, just as with extension cords. The voltage drops will add, just as in any series circuit.. . . the whatever-length of the 2-0 will drop the voltage that that length of 2-0 will at the actual load current, and the 6" of #2 will drop the voltage that 6" of #2 wil at the same current.
Still, even knowing that, if I have to join extension cord of different sizes, there's just something inside me that makes me want the heaviest cord closest to the source.
Voltage drop is based on the resistance of the entire conductor length. It doesn't matter if you had a smaller conductor at the beginning, middle or end of the run. As long as the smaller condcutor is of adequate size splicing a small length of conductor on to allow it to fit into the lug is acceptable.
The only Code reference needed is 240.4. As long as the conductor is protected at it's ampacity, it meets Code.Is there a reference in the code where this is allowed or can this be figured into the formula.In the past I special ordered a breaker with larger lugs .
You can use your standard voltage drop formulas. Say 40 amp breaker, #8 conductor 12" long spliced onto a 2/0.. Almost no voltage drop at the end of the #8. From the splice point you can figure the voltage drop on the remainder of the circuit
It's just a #2-sized-wire circuit that has a larger conductor in a part of the run. The portion that is still #2 is not suddenly a problem.It just doesn't seem wright to splice a smaller wire at the source as Larry said but if the math says its good its good at least for this code cycle.
I am curious about the best way to deal with this situation. Lets say you have a 125 Amp circuit and because of the length you end up with 2/0 copper wire. The 125 amp circuit breaker lugs are not big enough to accommodate wire that large. I've encountered jobs where someone has just trimmed off enough strands to make it fit but I don't think that would pass inspection. What would be the acceptable method for dealing with that?
Thanks
I've runa 20a circuit in #12 to a J-box on an outside wall, extended it across a parking lot in #6, and then back to #12 at the far end.
By saying "at least for this code cycle" you imply that you believe the option is something that should be removed for future codes. Why do you feel this way? It's a perfectly safe, compliant installation.It just doesn't seem wright to splice a smaller wire at the source as Larry said but if the math says its good its good at least for this code cycle.