Changing a 120v receptacle to 240v

Status
Not open for further replies.

tom baker

First Chief Moderator
Staff member
I don't see a safety concern with re-identifying the white wire, I suppose the CMP thought if it was in a raceway you should have pulled the right wire to start with, or another could be pulled in easier than running a new cable.

It is a code violation. CMP drew the line at 4AWG for re identifying. Most electricians have re identified 6 and 8, not excuse not to repull a black or red. Use the white to pull in a red.
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
You cannot re-identify a white insulated conductor in a raceway. It is bs, yet that is the rule.

I believe this is because the possibility of it being pulled to a j-box and spliced between a panel and it's final destination is higher.
 