If you sleeve an insulated ground wire with a piece of EMT say 15' long, do you need to bond both ends of the pipe or does that only apply if the ground is bare?
infinity said:Yes, you must bond both end if a ferrous conduit contains a GEC.
chevyx92 said:What if it's not a GEC? What if it's just an equipment ground?
No it's just a ground ran to a telephone board, thats it.infinity said:Then it must be run with the circuit conductors not in a separate conduit by itself.
chevyx92 said:No it's just a ground ran to a telephone board, thats it.
Thanks and pvc is normally what I would do but when the specs say " No PVC above slab" then I can't. And they were picky about when our pvc emerged from slab, to immediately change over to EMT. So this is why I was asking. Thanks for the help.paul said:That would need to be bonded to the raceway at both ends. It's easier most times to just locate it in PVC raceway.
Thank you.raider1 said:800.100(A)(6) for Communication circuits.
Chris
Sorry to confuse. We call the threaded fitting that we use to bond the wire to the pipe a choke. Guess the wording doesn't fit the purpose huh?raider1 said:Actually the choke affect is what you get if you don't bond the GEC at both ends of the ferrous metal raceway.
Chris
You mean a grounding bushing?Dave58er said:Sorry to confuse. We call the threaded fitting that we use to bond the wire to the pipe a choke. Guess the wording doesn't fit the purpose huh?
No, the fitting I'm talking about screws to the end of the conduit like a bushing.chevyx92 said:You mean a grounding bushing?