The beginning of 334.15 says, In exposed work, except as provided in 300.11a. cable shall be installed as specified in 334.15a through c.
according to this the only exception to the rule is 300.11a, it does not say unless allowed by other parts of the code, so with that said I believe that 334.23 is more about protection then exposed and since it allows running across the top of the joists in attics not accessible by permanent stairs or ladders as long as it's not within 6' of the hole I feel this shows that running across the joists is not prohibited. you would think crawling around in an attic and stepping on the wire would be more of a hazard then in a crawl space stapled to the joists. Just my opinion.
according to this the only exception to the rule is 300.11a, it does not say unless allowed by other parts of the code, so with that said I believe that 334.23 is more about protection then exposed and since it allows running across the top of the joists in attics not accessible by permanent stairs or ladders as long as it's not within 6' of the hole I feel this shows that running across the joists is not prohibited. you would think crawling around in an attic and stepping on the wire would be more of a hazard then in a crawl space stapled to the joists. Just my opinion.